Horticattleman":2g5am0so said:What good is pressure with no flow!?
The static pressure means nothing when you turn on the shower. It is dynamic pressure that constitutes the flow.
BHB you are right in saying it is all about flow, BUT using a pipe too small would make the velocity so high that it wouldn't be able to sustain the flow.
If it is off of a municipal supply, more than likely you are gonna be running with at least 50 psi. and lets say about 20 GPM through a 3/4" meter. The pressure loss on 2" Class 200 pipe(which is less than more expensive sch 40) would be .26 per hundred, or a total psi loss of 6.864.
p.s. RAB I'm looking at my chart here on my desk and 1" pipe would have a PL of 3.11 per hundred for a total of 82.104. Probably better not suck on it, it may pull you through it! AND the velocity would be maxed out at 4.61 FPS. Anything over 5 FPS is dangerous.
I recommend running 2 or 2.5" class 200 if you can get in 20' joints in your area.
Finally! Someone who knows water piping!
I might add the Class 200 pipe has a larger inside diameter than the Schedule 40 and will carry more water.
I would also put in a bigger meter..............